Topic4a Fire Safety
Topic4a Fire Safety
Topic4a Fire Safety
Junaidah Jailani
FIRE SAFETY
Principles of Fire
Passive Fire Protection
Building Utilization
Compartmentation
Means Of Escape
Active Fire Protection
Fire Detection System
Fire Extinguisher
Sprinkler System
Mechanical Compartmentation
Fire Safety Rules & Regulations
DEFINITION OF FIRE
According to NFPA
Fire: A rapid oxidation process with evolution of light and heat in varying intensities.
DEFINITION OF FIRE
Fire is a combustion or burning, in which substance
combine chemically with oxygen from the air and typically
give out bright light, heat and smoke.
PRINCIPLES OF FIRE
Fuel (in a nongaseous state) does not burn directly. When heat applied to a fuel, it
produces a gas. This gas, combined with oxygen in the air, burns.
Understanding the concept of the fire triangle is very important in correctly constructing
and maintaining a fire.
PRINCIPLES OF FIRE
The three sides of the triangle represent air, heat, and
fuel. If any of these removed, the fire will go out.
The correct ratio of these components is very important
for a fire to burn at its greatest capability.
Causes of fire:
Short circuit
Careless and unaware attitude among users
Dangerous activities held in building
Overheating
Pipe Leakage
Intentionally burning
CLASSES OF FIRE
WHEN DECIDING ON WHAT FIRE PROTECTION IS APPROPRIATE FOR ANY GIV EN
SITUATION, IT IS IMPORTANT TO ASSESS THE TYPES OF FIRE HAZARD TH AT MAY BE
FACED.
Class
A
Type of Fire
Fires that involve flammable solids such as wood, cloth,
rubber, paper, and some types of plastics
DEFINITION :
BUILDING UTILIZATION
Building utilization mean the number of persons using an
undivided space, such as a meeting room, classroom,
auditorium, hotel room or stadium.
As with building codes, fire-protection authorities often set
a limit on the number of people that can occupy a space.
Reason of limitation number of person are :
To ensure occupant must be able to leave the
building through the available number of exits in a reasonable
amount of time, without tripping or trampling each other In a
panicked situation, possibly blinded by smoke.
COMPARTMENTATION
Compartment means any part of a building which is separated from all other
parts by one or more compartment walls or compartment floors or by
both such walls and floors; and for the purpose of the Part, if any part of the top
storey of a building is within a compartment, the compartment shall include any
room space above such part of the storey. (UBBL: Part VII)
The purpose of compartmentation is to limit the spread of fire, smoke and flue
gases
Examples of compartmentation :
1. dividing office area into working place, office equipments room ( photostate &
paper shredder machine ) and storage area ( papers, files)
2. dividing hospital area into treating room, operation theater and chemical storage
area
COMPARTMENTATION
Method of compartmentation :
The construction of such compartments and all its components must
focus to achieve fire resistance rating which all components are
subject to stringent Listing and approval use and compliance in countries,
where product certification is mandatory.
Type of component :
1)
2)
INTERIOR
FURNISHING /
CEILING
Spraying
fireproofing to
the ceiling using
a gypsum based
plaster
MEANS OF ESCAPE
DEFINITION :
OSHA define an escape route or an exit route as a
emergency exit in
Stockholm's underground
station "Universitetet"
MEANS OF ESCAPE
FIRE DETECTION
1)Alarm
2)Manual call point
Alarm Trigger
Smoke Detector
Heat Detector
FIRE SUPPRESSION
* Foam riser
3) Smoke Extraction & Ventilation
FIRE EXTINGUISHER
PORTABLE FIRE EXTINGUISHER
FIRE EXTINGUISHER
AUTOMATIC FIRE EXTINGUISHER
1) Sprinkler system
When one or more of the automatic sprinklers is exposed to for a sufficient time to
a temperature at or above the temperature rating, it opens, allowing the air in the
piping to vent from that sprinkler.
As the air pressure in the piping drops, the pressure differential across the dry
pipe valve changes, allowing water to enter the piping system.
Water flow from sprinklers needed to control the fire is delayed until the air is
vented from the sprinklers.
For this reason, dry pipe systems are usually not as effective as wet pipe systems
in fire control during the initial stages of the fire.
Direct System
In-Direct System
Dry System: No Water in range pipe
Wet System: Water Ready in range pipe
SPRINKLER SYSTEMS
Wet Pipe Systems
By a wide margin, wet pipe sprinkler systems are installed
more often than all other types of fire sprinkler systems.
They also are the most reliable, because they are simple,
with the only operating components being the automatic
sprinklers and (commonly, but not always) the automatic
alarm check valve.
An automatic water supply provides water under pressure
to the system piping.
SPRINKLER SYSTEMS
Dry Pipe Systems
Dry pipe systems are installed in spaces in which the ambient temperature
may be cold enough to freeze the water in a wet pipe system, rendering the
system inoperable.
Dry pipe systems are most often used in unheated buildings, in parking
garages, in outside canopies attached to heated buildings (in which a wet
pipe system would be provided), or in refrigerated coolers.
Dry pipe systems are the second most common sprinkler system type.
The piping is filled with air below the water supply pressure.
To prevent the larger water supply pressure from forcing water into the
piping, the design of the dry pipe valve (a specialized type of check valve)
results in a greater force on top of the check valve clapper by the use of a
larger valve clapper area exposed to the piping air pressure, as compared to
the higher water pressure but smaller clapper surface area.
Increased complexity - Dry pipe systems require additional control equipment and air
pressure supply components which increases system complexity.
Higher installation and maintenance costs - The added complexity impacts the
overall dry-pipe installation cost, and increases maintenance expenditure primarily
due to added service labor costs.
Lower design flexibility - Regulatory requirements limit the maximum permitted size
(i.e., 750 gallons) of individual dry-pipe systems, unless additional components and
design efforts are provided to limit the time from sprinkler activation to water
discharge to under one minute. These limitations may increase the number of
individual sprinkler
Increased fire response time - Because the piping is empty at the time the
sprinkler operates, there is an inherent time delay in delivering water to the
sprinklers which have operated while the water travels from the riser to the
sprinkler, partially filling the piping in the process
FIRE SPRINKLER
HYDRANTS
Fire hydrants consists of hose reel and riser.
HYDRANTS SYSTEM
Dry riser No water in riser pipe
Wet riser Water ready in riser pipe
Explain TWO (2) types of Fire Safety System in a building (10 Marks)
DEFINITION OF
FIRE:
DEFINITION OF
FIRE SAFETY:
Fire Prevention,
Control & Extinguishment For A Certain
Protection In The Aspects Of
Example:
Consider a natural gas flame, such as from a stovetop burner. The fire can be
extinguished by any of the following:
turning off the gas supply, which removes the fuel source;
Enforcement
Engineering
Security
Maintenance
Good Housekeeping
Once the construction finished; the building itself will again required to be
inspected before approved by JBPM.
Designing & installing building services so that they do not assist the
spread of fire, smoke or any toxic fumes.
Designing & providing adequate & safe escape route for the occupants
of the building
Selecting materials for the construction which will not promote the
spread of fire or generates hazardous smokes.